埃德蒙顿华人社区-Edmonton China

 找回密码
 注册
查看: 3122|回复: 4

[技术互助] Any input on Cutler-Hammer Starter?

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 12:56 | 显示全部楼层 |阅读模式
本帖最后由 td456 于 2010-3-26 14:14 编辑
' C# u* `2 I$ @7 R
0 z6 I6 d+ y- P! r( ^Two  cutler –hammer advantage  starters are  doing the same thing:
% G8 B0 ?1 P- w% z, r After start 2-3 times, they will quit working, if you toggle the  start and stop buttons on DCS screen  , you will get another 2-3 running before they quit working again.
/ Y8 h: m% K% MIt is a cycle.
; [/ h, p6 y: F4 J: C
% W7 @! ^" j6 X" @We isolate the network control and use the local start and stop only, the problem remains.8 I+ x" l4 \- y+ \) s
Swap one of the defective buckets with a good one, the new bucket works fine.
5 G; D5 @  i% O1 J$ ^! sThe problem should be inside the bucket.. F! _, g8 l6 T! b4 y- P+ z7 l

. Z; m% P3 E; B  EWhen the problem happened, we observed that  the contactor has a pulling action but will not seal.4 n) l8 N/ x" y7 w
Use a terminating screw divers to push in the contactor, it will not seal either.0 p+ j6 C6 q3 h" r0 @4 P
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we  bought two new control circuit boards and replaced the old ones, the problem is still the same.4 A/ k* H2 r% {# b6 z9 x3 W

8 h5 `, p9 V( N0 z9 f0 n* o$ jThe next thing we can think of  is the coil, we took the coil out to have a close look.
/ I7 r& w  G2 \- ]They  have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered  the connection and tried again.
# e: M% w! \, i% |, R1 k$ S8 D8 L It is getting better  this time, we have 7-8 times of running before it quit working.
; G) W/ C1 n* ^/ G6 @( r' ~
: o4 E3 S) C, o- t+ y; cThe coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. - F. F2 B! T9 g6 V

9 n$ I  m7 C% f+ ADo you guys have any input on this issue?
鲜花(1) 鸡蛋(0)
发表于 2010-3-26 17:07 | 显示全部楼层
有时候主接触点太脏,也会造成启动器无法正常工作
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 17:37 | 显示全部楼层
本帖最后由 贾电工 于 2010-3-26 18:38 编辑 / Q% A' h$ _( B1 |7 Y
, b4 Y# A2 v/ u+ W% W/ f
中国人在这里最好说中国话!说英语或想学英语请人到洋人论坛!
鲜花(7) 鸡蛋(0)
发表于 2010-3-26 17:42 | 显示全部楼层
Don't know cutler –hammer advantage  starters very well, but had been worked on AB switch gears for a little while, which has two different coils, one to pull the vacum bottles up which employs larger current, another one uses less current to hold the connection---if the second coil fails, it won't be able to seal the connection.0 @9 e' G8 n5 b
Since your cutler -hammer works couple times,  I guess 侠客行 is right, or the sealing connection is just worn out.
鲜花(0) 鸡蛋(0)
 楼主| 发表于 2010-3-26 17:55 | 显示全部楼层
2# 侠客行
5 w2 b9 N( v* j. P9 s4 K- x% ]也想到这一点,不过这是新装的设备。% W6 t6 Q$ V9 ?; S" X; n8 T
检查过触点没问题。