Two  cutler –hammer advantage  starters are  doing the same thing:: f3 D( D. d9 T' r+ `+ Y
After start 2-3 times, they will quit working, if you toggle the  start and stop buttons on DCS screen  , you will get another 2-3 running before they quit working again.
, u7 a# z  _0 wIt is a cycle.
5 a% g7 v" h6 k0 E8 M& @0 Z
* t- L! `5 @6 g3 j$ n6 L+ GWe isolate the network control and use the local start and stop only, the problem remains.8 S; @" r5 F6 ?& J6 [
Swap one of the defective buckets with a good one, the new bucket works fine.6 r  u8 m1 u/ R5 _) i% S2 t5 E
The problem should be inside the bucket.
, Y8 c% A7 q4 N/ P5 J% V- K. A( R4 O. y4 M$ v" r) M- ~) ~
When the problem happened, we observed that  the contactor has a pulling action but will not seal.
! U! M: f# I- Y. O! B. z2 o+ W& mUse a terminating screw divers to push in the contactor, it will not seal either.
; c# e# H5 }" G3 q4 O) RConfirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we  bought two new control circuit boards and replaced the old ones, the problem is still the same.+ o. `( b  K8 i2 O

1 n5 n+ n+ a& L7 |3 \& _The next thing we can think of  is the coil, we took the coil out to have a close look.
4 Q. `# x2 S& g* j" y3 ZThey  have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered  the connection and tried again.
# Y; A# H# `, ]/ q+ v+ B" G It is getting better  this time, we have 7-8 times of running before it quit working.   s& ?. u; _) V; e" K' `# h) t
" R) ~% g! C8 u: z. c$ B5 D
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. 5 g8 [3 P9 }$ P

0 w( M) _# U: p4 r! IDo you guys have any input on this issue?
大型搬家
鲜花(1) 鸡蛋(0)
发表于 2010-3-26 17:07 | 显示全部楼层
有时候主接触点太脏,也会造成启动器无法正常工作
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 17:37 | 显示全部楼层
本帖最后由 贾电工 于 2010-3-26 18:38 编辑 6 p6 ?6 g  T2 C: G$ k4 m. `/ @0 }2 \

2 D5 k+ G/ ~5 ^1 O+ W7 @中国人在这里最好说中国话!说英语或想学英语请人到洋人论坛!
大型搬家
鲜花(7) 鸡蛋(0)
发表于 2010-3-26 17:42 | 显示全部楼层
Don't know cutler –hammer advantage  starters very well, but had been worked on AB switch gears for a little while, which has two different coils, one to pull the vacum bottles up which employs larger current, another one uses less current to hold the connection---if the second coil fails, it won't be able to seal the connection.1 U9 {; e* W6 ?" w( ]& i
Since your cutler -hammer works couple times,  I guess 侠客行 is right, or the sealing connection is just worn out.
鲜花(0) 鸡蛋(0)
 楼主| 发表于 2010-3-26 17:55 | 显示全部楼层
2# 侠客行
  F! I! X% }$ h3 z/ t3 f$ ~也想到这一点,不过这是新装的设备。, U: u* j6 S8 J& j0 O# t
检查过触点没问题。